Let me jump in. Since Jamestown Advanced makes the electric boxes perhaps I can make some general comments.
There are three receptacles found in the typical electric box in an RV park. One is 20 amp, GFCI protected. It is generally unsuitable for us to use as a power source for the bus because the way most of our conversions are set up the ground is not established until the transfer switch sees incoming power, and because of that the GFCI will trip. It can be used as a site power outlet such as for a vacuum or any 120 Volt device, but is generally not suitable for our coaches. There are exceptions however. I think Thompson coaches are set up so when there is incoming power it establishes a ground and because of what is called a "soft start" it does not trip the GFCI because it does have a ground connected.
The 30 amp receptacle is an RV specific one and it is 120 volts like the 20 amp receptacle.
The 50 amp receptacle is a completely different animal. It is actually two 120 volt legs each providing 50 amps of power. Depending on how the coach is wired it can provide 100 amps at 120 volts or 50 amps at 240 volts. When Willis mentions he only has 30 amps per leg, that means he can use his 50 amp plug, but if he pulls more than 30 amps from either leg he will trip the breaker in the distribution box. It is probable the owner of the facility did not want excessive electrical use so he limited it by installing 30 amp breakers. I suspect however because he uses a 50 amp receptacle the codes required him to pull heavy wire for 50 amp service.
So specifically 20 amp receptacle is 20 amps. a 30 amp receptacle is 30 amps, but a 50 amp receptacle is 100 amps. If whoever named the receptacles as 20, 30 and 50 instead said 20, 30, and 100 there would be less confusion.



Reply With Quote