It works fine, BUT there are a couple of caveats. Remember that a 50A circuit is really two 50A legs, and the PT-50 measures both. A 30A circuit is one 30A circuit, so generally a 30-50 adapter joins both of the 50A legs together. The readout on the PT-50 will still attempt to show each leg, even though they are the combined. I'm pretty sure you have to double the amperage readout to get the real 30A amperage. For example, if my battery charges are each drawing 3A, then the PT-50 will indicate 3A per leg. The total 30A circuit draw will be 6A.Just wondering, is it OK to use the EMS-PT50C on a 30 amp connection using a 30 amp adapter?