Mike- That is the same unit I have however it's spent it's life in the box until yesterday when I put it in line to help troubleshoot. With that very surge protector in place, it wouldn't allow any power (on either side) to pass through). I just moved to a different RV Park and am getting back to troubleshooting again. I put the surge protector in line and a pen to go record the codes. I could hear that no roof A/C's went back on so I went inside to check the inputs on both inverters. Then, the power kicked on. Upon further reading of the owners manual I now learned that the surge protector takes a pause before allowing power through. So shore power and generator power are both eliminated as I also have input power on both legs on the panels.
I think I may have a bad GFI on one of the 110 outlets. I'm not sure but I'll explain.
Each side of the bus (on my Royal) has multiple 110 outlets of course. Only one of them as a GFI outlet. If that GFI is tripped, all the other outlets loose power also. We'll the GFI on the passenger side (the side I'm having trouble with) is not making any clicking noise when I push it from Test to On like the other (working correctly) does when I "Test" it.
Question: If no power is being supplied to that outlet, should I still be able to detect a clicking upon toggling the buttons ? I don't know. There is no clicking so I don't know if it is because of no power thorough or bad GFI.
(Answers to Gary's Questions follow)
Jeff. Is your toilet 12 or 24 volt or 120 volt? The inverter is for 120 volt loads.
>>>> When I read this I thought "Hmmm. I didn't notice anything electrical at all on the toilet when I removed it and rebuild the guts a few years ago". It's a Microphor. I believe it is totally air powered. I do not have a breaker anywhere for the toilet but there is a 5 amp breaker for the air pump for the toilet on the 12 volt panel. The light on the switch for the air pump comes on, but the pump doesn't come on.
What else is not working?
>>>>> The microwave, washer and dryer, and all the outlets on the passenger side. The TV in bedroom IS working along with all that A/V that goes with it (DVD, Bose, ETC) and that is on the passenger side). Not sure if relevant or related yet.
It sounds like yo have identified several issues;
1. Your shore power surge protector no longer works. Are you still getting 240 volt into the Panel?
>>>>>> Yes
2. Your buss fuses on the battery side of the Invertor is OK. These batteries are usually in parrallel so your going to get readings on the battery side of the fuses.
>>>>>> Not positive what you mean here but I do believe I've eliminated those fuses as being the problem.
3. You can not get correct voltage from the shore recepticle to the bus. Hve management test shore power.
>>>>>> Addressed I think and shore power at two different RV parks with same symptoms. Same symptoms on Gen power as well.
4. You checked Generator which when started should run all 120 volt loads as well.
>>>>>>>> Yes
5. You replaced coach batteries recently. Check wires.
>>>>>> Checked. However could possibly still be something in the battery bay. Still trouble shooting.
Further: My inclination is that it is not an inverter problem but I'm not sure. There is a tiny red LED viewable on the interior of the inverter though the grate. It goes on and off when I turn the inverter to the "off" mode on the remote as it should. It's just the toilet and the passenger side outlets and the microwave. Water pump working and everything else that I can tell. Continuing the battle and trouble shooting.
Any input on the GFI not making the clicking would be very useful. Replacing that is an easy and cheap attempt at the remedy even if it wind us not being the problem. Will check back here and wait until tomorrow for any additional input however before changing it out.