Had Featherlite rebuild my HVAC basement unit about 4 years ago (new compressors, new fan motors, new capacitors, new control board, new thermostat), everything ran well afterwards. About a year ago I was at a site that had very low voltage and it fried my fan motor and the control board. I replaced the fan motor and control board then installed the Micro-Air soft starts on the units. The system has worked flawlessly for just short of a year, but now the 1st stage compressor is dropping out after a couple of days of use. I can restart the system and it will work fine for a couple of hours then 1st stage drops out again. It can be immediately restarted but then only runs for a 1/2 hour or less.
Compressor is running at 7-8 amps (well within normal range), shot relays on circuit board with thermal gun, everything is within normal range, unit cools fine when running. Start and run capacitors tested within range but weak so I replaced all of them (fans & compressors). System went back to running normal for 3 days (cycling off & on), but now 1st stage is starting to drop out again yet still restarts immediately without any issues.
It’s got me baffled, everything operates normally within parameters but then 1st stage suddenly drops out, yet will restart and run without issues immediately. Doesn’t make sense, something should be showing out of normal operating range before failure.
What am I missing?
Chuck