Quote Originally Posted by Gil_J View Post
Your 240V drawing is confusing me. First, can I assume you are talking ACV? If so, what will you do with 240VAC that's not split-phase?
The HP power supplies do not care what form of higher voltage that you have as an input since they are designed to be used around the world. It could be split phase or a tap off of two legs of three phase power which is 208 volts, they adjust to a wide voltage range.

The key operating point is that aggregate power generation of the combined power supplies is greater than what the solar charge controllers can absorb. It's the solar charge controllers job to manage and account for the type of house batteries that you are using.

In my case I plan to split the power out via the battery isolator to my two other solar charge controllers when charging via the generator.

I suppose I could do the same when plugged into 50 AMP service, though generally when you do that; you are going to stick around for awhile, so not the time pressure you have when running a generator.