Originally Posted by
jack14r
I have a question,at most of the primary electrical panels the neutral and ground are not bonded but if there is a second panel aren't the neutral and ground bonded?
Per the NEC, the Service Entrance Panel (or main breaker panel after the meter) has the ground bar run to an earth ground rod, and all the neutrals and grounds are together on the same bus bar in this panel. EVERYWHERE else, they are kept separate/isolated, thus the "ground" or bare wire from there on out is NOT a "current carrying conductor." The white/neutral wire IS however a current carrying conductor, and will not be at the same potention as earth ground.
Hope that helps.
Ben Cummings
U.S.A. Luxury Coaches, LLC