    Default Generator cooling fan fix

    On my way thru Tennessee my generator shut down due to over heating. A little trouble shooting and I discovered that the 120 Volt cooling fan that draws air thru the radiator was not working. I called Royale Phoenix and asked for help. Dan and Glen were a great help. Basically it could be 1 of 3 different issues.
    1. A small breaker on the generator that sends power to the fan.
    2. A "start capacitor" for the motor
    3. The electric motor for the fan

    Glen said it is almost always the start capacitor. So I had him send one to my next stop. I received it today, installed it in 5 minutes and luckily that was the problem. The cooling fan is working again.

    Upon close examination of the bad capacitor I discovered that it was swollen at the top. I did not notice it until I compared it to the new one.

    Cost
    $16.82 for the capacitor
    $15.92 for 2 day shipping.

    For once an easy and fairly inexpensive fix. Could have been worse.

  2. #2
    Join Date
    Jun 2011
    Location
    Cincinnati
    Posts
    5

    Default

    Hello Andre, I have a 2006 Royale and am looking for the cooling fan motor, can you give me a hint where to look.
    Thanks
    Rob Hollaender

    Update: Chuck talked me throught it, Thanks Chuck. It is located in the gen compartment, some disassembly required.
    Last edited by rphollaender; 10-07-2011 at 10:40 PM.

  3. #3
    Join Date
    Apr 2008
    Location
    no where
    Posts
    439

    Default

    Rob,

    I have a 1999, so it may be different. My cooling fan is behind thee generator radiator. I would need to pull the radiator to get to it. Luckily I only needed to change start capacitor which was in a steel box just above the radiator.

  4. #4
    Join Date
    Mar 2009
    Location
    Harrison
    Posts
    623

    Default

    Andre, what kind of generator set do you have?

  5. #5
    Join Date
    Sep 2009
    Location
    Northville, MI
    Posts
    127

    Default

    So, after reading about Andre's adventure and chatting with Rob about his, we are awakened at 4am by a very loud squealing noise!
    We're dry camping at the Horseshoe casino in Shreveport on our way home from POG X.
    Turns out that the cause is a failed bearing on (wait for it....) the generator cooling fan. It ought to be simple to repair but it isn't going to happen in a parking lot, we'll just find a hookup for tonights stay.
    Cheers,

  6. #6
    Join Date
    Jun 2011
    Location
    Cincinnati
    Posts
    5

    Default

    Hello Chuck, my problem turned out to be a simple loose breaker connnection. My start relay is also located in a junction box inside the gen compartment, same as Andre's.

  7. #7
    Join Date
    Aug 2009
    Posts
    507

    Default

    Those generator fan start capacitors are typically 5MFD 370 VAC devices and are available at most HVAC outlets for a few bucks. Here it is at Graingers, although they don't appear to carry it anymore: part number: 5M003. http://www.grainger.com/Grainger/wwg...N=0&sst=subset

  8. #8
    Join Date
    Jul 2010
    Location
    Lufkin
    Posts
    401

    Default

    Chuck... did you go over to the Jack of Diamonds for the night? Did you get your geberator fixed? Hope it all went well for you.
    Diane

    Quote Originally Posted by Charles Spera View Post
    So, after reading about Andre's adventure and chatting with Rob about his, we are awakened at 4am by a very loud squealing noise!
    We're dry camping at the Horseshoe casino in Shreveport on our way home from POG X.
    Turns out that the cause is a failed bearing on (wait for it....) the generator cooling fan. It ought to be simple to repair but it isn't going to happen in a parking lot, we'll just find a hookup for tonights stay.
    Cheers,

    Larry & Diane Byrd
    Lufkin Texas.
    2005 Liberty Elegant Lady H3-45
    1998 Vantare H3-45 D/S SOLD
    2016 Cadillac Escalade ESV 4WD

  9. #9
    Join Date
    Sep 2009
    Location
    Northville, MI
    Posts
    127

    Default

    Rob, glad the problem was simple to fix; sorry the diagnosis was such a PIA. Hope your trip came off as planned.

    Di we pulled in to the Horseshoe and stayed there. All was good until the generator cooling fan woke us up at 4:00 am. The failed bearig is part of a stock Dayton cooling fan that was easily sourced at Grainger. Instead of fooling around with the old parts we decided to simply replace the whole fan assembly. Work is all done and better (in my opinion) than the original.

    Hi to all from Barbie. She is pretty much recovered from her tumble and looking forward to the next opportunity to ride a Segway. The warmth and concern shown by so many towards her are more indication of the nice people we have met in POG.

    Thanks to all