Thread: CruiseAir Temp Difference

Hybrid View

  1. #1
    Join Date
    May 2019
    Location
    Leesburg
    Posts
    534

    Default CruiseAir Temp Difference

    My Front CruiseAir unit is seeing a 10-to-12-degree difference between the intake vent and outlet vents in a shaded garage with outside temps of 80 deg. Somewhere back in the old fussy brain cells I think I remember the temperature difference should be 20-to-22- degrees if the system is working properly.
    Can someone confirm or deny these numbers.

    Chuck
    Chuck & Katrina
    2000 Featherlite
    H3-45 Double slide
    2014 Jeep Grand Cherokee Diesel

  2. #2
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    Not sure about CruiseAir specifically but yes, 20 deg would be good. A 10 degree delta will never cool your coach.


    Mark and Debbie Fratto
    1998 Parliament

  3. #3
    Join Date
    May 2019
    Location
    Leesburg
    Posts
    534

    Default

    Started looking deeper into things because the front CruiseAir has never really cooled well, even after having the unit behind the bumper replaced. Found the copper line (larger one) going into the evaporator in the front cabinet has been bent to tightly and has quite a kink in it.
    Not all the knowable on AC systems but have to imagine that kink is reducing the freon flow and in turn effecting it's overall performance.

    Chuck
    Chuck & Katrina
    2000 Featherlite
    H3-45 Double slide
    2014 Jeep Grand Cherokee Diesel

  4. #4
    Join Date
    Aug 2015
    Location
    Celebration
    Posts
    47

    Default

    Chuck
    What are your pressures on the front unit? A slight kink in the suction line should not affect it much, but a significant kink will. That kink was likely there the whole time, but now that you are searching an issue you noticed it and could be the culprit. Can you post a picture of the kink? The front evaporator plate (inside the coach behind the mesh filter) should feel wet. With a 10-12 degree split as you state, it likely is low on refrigerant. Check your pressures and adjust accordingly. If the kink is the culprit, it will also reflect in your gauges, primarily with a erratic or bouncy reading. The kink will cause it to improperly meter the refrigerant and pressure fluctuations in the gauges. The low pressure should be around 55-65 and high pressure should be around 225-275. This range is relative to your current ambient temp.
    Dane & Dana
    Central Florida
    95 Marathon

  5. #5
    Join Date
    May 2019
    Location
    Leesburg
    Posts
    534

    Default



    Dane:

    Here is a picture of the Kink. I am the 3rd owner, when going through the paperwork I noticed lack of cooling in the front unit (The one I found the kink in) has been a complaint since the first owner. Compressor failed shortly after I purchased the coach 3 yrs ago. Had AAP in VA replace the front unit. It cooled but never that well. Think I discovered the reason why it has never cooled well. Hopefully before it has ruined my new compressor.
    Not going to be easy to access, buried under flooring that's under the cabinet.

    Chuck
    Attached Images Attached Images
    Chuck & Katrina
    2000 Featherlite
    H3-45 Double slide
    2014 Jeep Grand Cherokee Diesel

  6. #6
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    Good catch. You are right, there is no way that this will allow the system to work at its rated capacity.
    Keep us posted on performance after you correct this problem.


    Mark and Debbie Fratto
    1998 Parliament