    Default Roof Air Conditioner

    A roof air conditioner and heat pump that is controlled by a central thermostat. When air or heat is called for on this unit, the fan comes on as normal, but the compressor never tries to start. Is there anything other than a bad compressor that would cause this problem? I feel relatively sure it is not a thermostat problem.
    Dale & Paulette

    "God Loves you and has a plan for your life!

  2. #2
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    How about something like a start capacitor or overload of somekind internal to the unit?


    Mark and Debbie Fratto
    1998 Parliament

  3. #3
    Join Date
    May 2012
    Location
    Beverly Hills
    Posts
    4,652

    Default

    Quote Originally Posted by dale farley View Post
    A roof air conditioner and heat pump that is controlled by a central thermostat. When air or heat is called for on this unit, the fan comes on as normal, but the compressor never tries to start. Is there anything other than a bad compressor that would cause this problem? I feel relatively sure it is not a thermostat problem.
    Relay pn the control card or capacitor.


    Gil and Durlene
    2003 H-3 Hoffman Conversion

  4. #4
    Join Date
    Nov 2006
    Location
    Huntsville
    Posts
    3,135

    Default

    Thanks for the suggestions. I eventually found a wire that was not making good contact.
    Dale & Paulette

    "God Loves you and has a plan for your life!

  5. #5
    Join Date
    Mar 2013
    Location
    Chicago
    Posts
    3,988

    Default

    IMG_20220221_132623839.jpg

    IMG_20220221_132658862.jpg

    IMG_20220221_132726254_BURST000_COVER.jpg

    IMG_20220221_132739719.jpg

    IMG_20220222_100312478_HDR.jpg

    IMG_20220222_100326729_HDR.jpg

    Please I need some help with making the correct connections on a second hand roof air I have put in my trailer. The fellow who removed it unfortunately did not leave some wire tail leaving a colored wire tail on the spades identified with that yellow strip. The thermostat it all came from the same rv it worked great should be plug and play but I need to plug it in correctly or that magic smoke will escape and it will die.

    The thermostat does it require 12 v dc to function?

    If so is the blue wire 12v ground that's what it looks like to me?

    Thermo has heat mode that's not applicable here is there a wire for it u leave unhooked?

    4 of those wires coming off the thermostat connect to those 4 spades.

    What is GH and GL?

    Y is yellow??

    B is blue?

    What of the remaining 2?

    How do I where what??? Please help me.

    IMG_20220222_131628653_HDR.jpg

    IMG_20220222_131424883_HDR.jpg

    IMG_20220222_131455839.jpg
    Last edited by Joe Camper; 02-22-2022 at 02:32 PM.
    1990 Peterbuilt 377
    3406 B Caterpillar
    13 Speed Roadranger
    No Norgrens


    1 day on paper no machines

  6. #6
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    I believe that coleman is using the following:

    red is 12 volt
    blue is common
    green is high speed fan
    gray is low speed fan
    yellow is call for cooling
    white is call for heat


    Mark and Debbie Fratto
    1998 Parliament

  7. #7
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    red is 12 volt
    blue is common
    green (GH) is high speed fan
    gray (GL) is low speed fan
    yellow is call for cooling or compressor
    white is for a furnace

    Yes, it needs 12 VDC to function
    Yes, the blue is ground
    Yes, leave the white wire for the furnace disconnected.


    Mark and Debbie Fratto
    1998 Parliament

  8. #8
    Join Date
    Mar 2013
    Location
    Chicago
    Posts
    3,988

    Default

    Ok

    Red to 12V.

    Yellow to Y

    Green to GH

    Grey to GL

    Blue to B

    White remains unhooked.

    Correct?
    1990 Peterbuilt 377
    3406 B Caterpillar
    13 Speed Roadranger
    No Norgrens


    1 day on paper no machines

  9. #9
    Join Date
    Apr 2019
    Location
    Arlington
    Posts
    787

    Default

    That’s what I would do


    Mark and Debbie Fratto
    1998 Parliament

  10. #10
    Join Date
    Mar 2013
    Location
    Chicago
    Posts
    3,988

    Default

    Thanks a million Mark I'm going to hook it up today.
    1990 Peterbuilt 377
    3406 B Caterpillar
    13 Speed Roadranger
    No Norgrens


    1 day on paper no machines