Log in

View Full Version : House electrical change to Tesla Battery modules



freds
03-01-2020, 12:04 AM
The house side electrical heart has been upgraded with Tesla Power!!!

https://www.crystalpoint.com/cpdownloads/public/outgoing/Freds/TeslaPower.jpg


Tesla Battery modules are attractive for reuse in solar or RV installations due to their energy density and cost.

You can get a recycled Tesla module for a bit more than the cost of a single BattleBorn battery and have more than four times the storage capacity.

To safely use and protect Tesla battery modules you need a BMS setup/configuration.

In my application I make use of the SimpBMS open source product/project and other components that I purchased from the British firm “Second life EV Batteries”.

Tesla doesn’t put a fully functional BMS on each module like you get with a BattleBorn battery.

This is because a typical model S or X Tesla has 16 modules, they use the approach of slave BMS’s with a master controller for the entire battery pack.

So, in short, every Tesla Battery module already comes with an integrated BMS module that is offline as it is waiting for a master controller to wake it up!!!

As you can see from my posted picture of this bay I have the following:

1. Two Tesla battery modules cased up and mounted
2. SimpBMS controller with display
3. Two solar charge controllers
4. 70AMP 24V to 12V DC-DC converter

Here's a picture of the touch display:

https://www.crystalpoint.com/cpdownloads/public/outgoing/Freds/TeslaBMS.jpg

In the next bay on the other side of the adjoining wall:

https://www.crystalpoint.com/cpdownloads/public/outgoing/Freds/Inverter.jpg

I have my 6KW inverter that can surge to 18KW and another solar charge controller.

Current storage is 10.4KW of power, that is reduced to 8KW in the interest of battery life and safety while charging while at the upper end of the charge zone. (Solar charge controllers will over charge two Tesla modules if permitted, restriction goes away with more modules).

I can post more details on this setup if people are interested.

Gil_J
03-01-2020, 08:40 AM
Interesting. A single BMS for a fair sized battery bank would seem to be either extremly sensitive or not as reliable. It would seem like a single cell may have to degrade too far for the BMS to react.

Can the bank be split into multiple 24V banks so additional BMS units can be installed? A Tesla us operating at a voltage well above 24V. How was the 24V bank created? That looks like an AIM Power inverter. I've installed a few and discovered they, like most high frequency inverters, don't like surges. They also have very limited configuration options. At least that is the case with the blue ones.

It's good seeing some try out other options.

freds
03-01-2020, 06:24 PM
The SimpBMS controller functions as the master BMS controller for your recycled Tesla battery modules and is based on open source projects that reverse engineered the protocol that Tesla uses to communicate with its battery modules. Each Tesla Battery module has a slave BMS that controls each module for balancing and reporting voltages and temperature for the module.

SimpBMS was initially developed for the hobbyist market of converting Gas Vehicles to Electric Vehicles using recycled parts from these vehicles.

However, the firmware does have a mode (ESS) for stationary use for Powerwall or in my case RV usage.

Also, note that the SimpBMS is heavily CAN based and can be used with other EV battery sources like LEV40 Modules, LEV50 Modules, BMW i3, E-Golf & GTE (slave PCB needed on all modules).

In the Tesla Battery modules every cell is individually fused which would blow if they got grossly out of sync with their compatriots. I am not really worried about the Tesla battery modules, as there are more than a million of them in use. Internally they are wired as 6 series of 74 parallel (6S74P) 444 cells.

My setup has the following following components:


Victron 24V to 12V DC to DC converter
Victron Color control head
Victron Solar charge controllers (3 EA)
3.5 KW of solar panels divided up into three separate zones
Singineer Inverter/Charger 6KW Tesla model APC6024DT 240/120V split phase power
Two Tesla Model S modules connected in parallel for a 24V pack acquired off of EBay.
SimpBMS for Tesla


I am using a fair amount of Victron hardware where it made sense to me; to go with SimpBMS approach as it supports a CAN interface to Victron control head and functions also as the battery monitor in this configuration.

So, no need to purchase a dedicated battery monitor as most people do.

I purchase the following SimpBMS related items from: https://www.secondlife-evbatteries.com/


SimpBMS 2.3 board configured for Tesla model S/X battery modules
NEXTION display pre-configured for SimpBMS
Used/Recycled LEM CURRENT Sensor CAB300-C/SP2
Used/Recycled OMRON CONTACTOR G9EA-3-CA-M2
Connectors package for the SimpBMS


If I was to do this again I might have gone with a Victron Inverter though they are much more expensive as they support a wider variety of power input voltages for driveway surfing. The Singineer charger functionality is only for 240V input and is fairly wimpy at a 2KW charge level.

I have some hardware laying around from my e-bike days; before I got my Tesla, that I am looking at integrating to give more charging flexibility, but that portion would definitely be a one off that would be difficult to duplicate.

My next phase is installing internet in the bus and adding a Pi based controller running Home Assistant and NodeRed for my automation, reporting and control functions.

The next major phase after that will be a DIY hydronic system that I am working on.

truxton
03-01-2020, 07:57 PM
Hi Fred

Im not much of an electric guy, understood about half of what you said but I know pretty soon the old way will be gone.

Looking at your pictures you have what looks like 2 water hoses running thru that bay with a whole lot of stuff under it. Are you concerned about that.

I was gonna be a smart ass and ask how many fire extinguisher's you had on board.

Later
bv

Gil_J
03-01-2020, 09:51 PM
Fred, you are definitely a hands on guy. Curious if you have considered housing the batteries in a fire box?

The hydronic heating system should be a lot easier than what you've accomplished. Have you decided which brand burner you'll use?

freds
03-02-2020, 04:17 PM
Hi Fred

Im not much of an electric guy, understood about half of what you said but I know pretty soon the old way will be gone.

Looking at your pictures you have what looks like 2 water hoses running thru that bay with a whole lot of stuff under it. Are you concerned about that.

I was gonna be a smart ass and ask how many fire extinguisher's you had on board.

Later
bv

Three fire extinguisher's and planning on lots of Internet of Things stuff on a standalone network, where there will be seperate fire alarms for all area's.

The inverter is purposely mounted about four inches off of the floor in case there is a leak in the shared bay.

The two hoses are to tap into the hot coolant feed from the engine to the drivers heater to warm the hydronic storage when driving.

When I get everything finished I will do more posts on the electrical and hydronic design on my update.

freds
03-02-2020, 04:37 PM
Fred, you are definitely a hands on guy. Curious if you have considered housing the batteries in a fire box?

The hydronic heating system should be a lot easier than what you've accomplished. Have you decided which brand burner you'll use?

The Tesla modules are very well engineered and in my opinion just need to be protected from mechanical damage. So no not going to do a fire box.

As to the burner I got a military new surplus Espar Hydronic D10 unit ($800.00) that was part of a arctic winterization kit for a large diesel generator. It's a 24V unit so fits well into my house electrical system.

I tend to cuss at the previous owners saying "what the heck were they thinking on all their various make overs/modifications!!!". Found paper work where the bus previously had a Wabesto unit when I quizzed the PO, he removed it to fix it and found out that it needed a replacement motor that cost $400.00 so decided not to replace it... Crap you can't fix what is not there...

freds
03-02-2020, 08:32 PM
Hey solar charging sort of goes live here in Soggy Seattle!!!


https://www.crystalpoint.com/cpdownloads/public/outgoing/Freds/SeattleSoggySolar.jpg


Not all of my static loads are running yet, but the Tesla battery pack gained a net charge while parked in the storage yard.

Next to be wired in and powered up is:

1. Cellular Data modem for always on Internet
2. Three POE data switches
3. Raspberry Pi 4 automation controller
4. Wify access point
5. Victron Color control display

Currently running is:

1. SimpBMS controller/battery monitor with:

a. Always on color display
b. LEM CURRENT Sensor CAB300-C/SP2
c. OMRON CONTACTOR RELAY G9EA-3-CA-M2
d. Two OEM slave BMS's on the Tesla Battery modules

2. Three Victron solar charge controllers
3. Victron 24V to 12V DC to DC converter driving the new 12V buss and float charging the 12V generator start battery.
4. Some minor 12V parasitic draw that I haven't tracked down yet, that totally drained the old house batteries.

PS. It's been raining all day....

Ck2hans
03-03-2020, 09:53 AM
Hay Freds:
Does that solar panel double as a spray sheild for the wheels too? LOL
Chuck

freds
03-03-2020, 12:01 PM
Hay Freds:
Does that solar panel double as a spray sheild for the wheels too? LOL
Chuck

Nope it's just temporary until I get it and it's brethren mounted on the roof. Though your question does spark an idea!

In looking at the placement of my windows, maybe I could make a an group of them that would pivot from vertical to horizontal to also function as a Sun Canopy? In that case it would be a spray shield for the right side drive axle when stowed.

In the meantime I am going to have to arrange to store it. I am thinking that I can simply mount a couple of 2x4's vertical to the bay wall orientation, on each side of one of the bays to make a slide in storage rack.

Joe Camper
03-03-2020, 03:35 PM
16243

I know you've got cloth awnings on the bus but I couldn't help myself when you mentioned putting a solar panel on an awning. This little hundred-dollar panel from Amazon charges to 8D gel batteries. It's the only charged source I use and it more than keeps those two batteries charged up for me for what little I need I have a small residential fridge and a little TV at night that I watch 3 or 4 hours and what I use by night this panel replaces by day and I could go indefinitely I just don't understand why solar is it more prevalent with the buses. I've mentioned it before they have solar fabric somebody needs to make the whole top side of the awning one big solar panel with solar fabric.

When you guys are boondocking on inverter it's really not necessary to leave the inverters constant on it's also beneficial if you turn them off because they're using voltage just idling whether there's a load on them or not. Usually it's the refrigerator that quite possibly could be the only constant load that you need to keep going if the weather is fair. So get to know your fridge see how long it takes for the compressor to cycle off and do some testing and run the inverter 4 an hour every three or four hours and when it's running make sure that the thermostat on the fridge is set all the way over to cold so it runs the whole time. huge battery Banks you guys got in them buses only God knows how long you could go with some solar panels if you didn't run the inverters constant on when boondocking. Coordinate your other loads with the runtime for the fridge and then just turn it on for the intermittent loads when you need them andthen turn them back off. How dare I even suggest this for Prevo. We should get together and have an Enduro camping contest let's go out to Quartzsite and see who can hang out the longest on the provisions that you carry out there with you wouldn't that be fun.

Great thread Fred have fun testing and playing around.

freds
03-03-2020, 04:12 PM
Hi Joe

I am definitely putting my system together with boondocking and places like Quartzsite in mind.

I agree with you about the inverter being a major draw while it is idling.

One target for the Raspberry Pi automation is an automatic sleep mode; if it detects that the cell phone's for occupants are not attached to the local wify (occupants present) and there is not a load (something cooking in instant pot) on the inverter for thirty minutes.

You would have to do that contest based on available solar levels, power consumed; with detriments for generator runs, etc.

Of course if I duplicate my home PC setup with multiple monitors and no solar input I can easily burn through my battery bank in a day.

PS. Another update that I am making to my humble home on wheels is to change the refrigerator over to a DC compressor.

Anthem
03-04-2020, 02:30 PM
Hey Freds, enjoyed reading your writeup of what you did. I almost went the Tesla S battery route as well. I didnt want to deal with a slightly non-standard voltage with that pack, as I think its using cells which sit at 3.7 instead of the more normal 3.2v x 4 cells that LiFePo4 cells work at. Glad you took it on, and hopefully it gives you good working margins. . .

I'm on my second lifepo4 install. This time using almost all Victron equipment as I love their bluetooth, victron connect, and vrm portal. Their inverters are awesome and I have a pair of them in split phase. Debating putting in an autotransformer to balance the inverters, but so far not too many problems with the split phase (outside of 30amp service).

The Victron controllers give you good manageabilty. They also now interface with some MFD devices in the marine world. So you can convert to NMEA2K and do some things on that front. The RV network and open marine one just hasnt taken off as much as NMEA2K still works.

Interesting choice on Pi. Its probably the cheapest and most flexible. Arduino might work better for battery bms type of work, but you have that covered. I had those same choices, but currently working off a PLC controller that does what I need to do. You may also want to look in to that, but it is a bit more costly than Pi, but the number of modules and things they have prebuilt is pretty extensive(proximity sensors, motion, etc). IFM makes some great mobile PLCs with CanNet network built in and all using CoDeSys development platforms. But again, pricy.

Anyhow, totally cool. Love to hear more as you progress. I'm also debating solar panels since there is so much real estate, but have to tackle a bunch of other projects up there.

Gil_J
03-04-2020, 03:28 PM
Ed,

Be careful going to a split-phase setup. The new NEC allows campgrounds to be wired with 3 phase power. So, your nominal 240V just went down to a nominal 208V.

How are you going to use an autoformer to balance the loads? Are you considering 2 autoformers, one per phase? In that case you could achieve a near balance in voltage, but I'm not following how you'll achieve load balancing.

You are dead on when it comes to advancements and acceptance MMEA-2000 compared to RV-C. RV-C was born at the downturn of the RV industry, so few wanted to invest in it. Frankly, NMEA-2K is far more robust and has widespread support. RV-C should simply die in favor of NMEA-2k.

Great info!

Anthem
03-04-2020, 11:36 PM
Gil yeah, I saw that. Probably on a post you made in some other. . I dont think we need to worry about 208 but the 104 vs 120 since technically the 50amp plug is two phase 120/240. But yes, its an issue. I have the victron Autoformer to balance the inverter outputs. . But I havent installed it as my powertech generator doesnt seem to care that L1 is more loaded than L2. .

Now, back to the input issue. yeah, that had me concerned as well. I have the Hughes Autoformer that will boost it 11% which will take it to an acceptable level. They claim it will keep the 2nd phase in-phase and the Victron in split phase will work without an issue. Have not tested as I havent installed it just yet.. . Lots of transformers to consider. But yes, the issue is there. But 104 might just be as problematic on an input as the split phase. The split phase to me - seems to be a bigger issue if I have to dogbone adapter to 30amp service as thats single phase and the Victron units in split phase - will only power one side when there is not a split phase input. Not too big an issue since the L2 side will just be inverted from the battery as L1 powers L1 through the inverter - which in turn is charging the battery back to whatever L2 is drawing (whew). Not ideal, but then again 30amp service isnt ideal. .

But i havent come across the 204 problem just yet. . . . but I know its there.

Gil_J
03-04-2020, 11:54 PM
Just so you know. The 3 phase power should have no effect on the 120V single phase. It's 120/208V because the phase difference is 120 degrees instead of 180 degrees of split phase.

Generators definitely prefer balanced power between the legs. Because of this Vantare use to have all 120V appliances and had there generators configured for 120V.

I'm still not certain how a transformer is going to balance leg loads. I'll have to look at the Victron transformer you referenced.

Anthem
03-05-2020, 12:14 AM
Oh sorry - yeah, 3 phase 208. Sorry, threw me off with the 204. lol. but if its split phase 208, what will happen with the split phase configured Victron is the same as if there was only one leg operational. The other one would fail to sync (unless I configured on the fly from 2P at 180degres to 3P at 120 degrees. But even if it failed to sync, it would take 120 on one leg in to one inverter and the other would continue to invert off the battery while the first one supplied loads on L1 and charged what was being removed from L2.

The other option is parallel. But you would have to split the inverters up in to completely independent units for this to work. As parallel requires the two to be in identical phase. The advantage for all of this is to keep one monitoring system. The displays can read a split phase or parallel system but it cannot read two systems. So unless I wanted to double all the front end displays and controllers (which is how the previous Heart Interface was) - then you have to go split or parallel. Some have gotten around the problem by autotransforming on the front end - which would take two legs and create its own 120/240 output(but this doesnt work for 3 phase 120 degree out of phase - well at least I dont know if it does or not). . So lots of ways to skin the beast, but unfortunately not all of them are perfect - as each has advantages and disadvantages.

The victron autotransformer takes two legs and because neutral isnt passed - it balances the output legs - up to 32amp differential.. PDF documentation here https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf

And agree with you. NMEA2k is so much further along than Silverleaf's implementation or RV-C. Even signalK is better.. . I seriously thought about running NMEA2k but it would have been overkill on an older bus. but I've done my boat completely in n2K. I think I might have 20+ maretron nmea2k devices on the network there reading DC amp,volts, AC amps,volts from various sources. Of course you need/want more information on a boat than in a motorhome. . .

freds
03-05-2020, 12:20 AM
I think the Victron inverters with the power boost feature will automatically adjust for the difference.

With my Tesla when I first got it; I had to charge at a hotel (unplugged a dryer) and with their wiring the voltage was at 198 volts, took 14 hours to charge the car instead of the expected eight.

I had arrived bone dry with 3 miles of range remaining!!! This was when their super charger network was first being built and had large gaps in the coverage.

freds
03-05-2020, 12:23 AM
First sort of sunny day with a single panel hooked up to the bus:

https://www.crystalpoint.com/cpdownloads/public/outgoing/Freds/FirstSunnyDay.PNG

Look at the last four days of production as that was days that a solar panel was actually hooked up and not simulating them with an external power supply (29V).

My panels are 72 Cell LG High Efficiency 375W Mono Solar Panels and I purchased ten of them used for $1,500. Thinking that I might be able to get anywhere between 7-9 panels installed on the roof.

The graphs show the last four days with a single panel propped up against the side of the bus. The first day was late afternoon hookup, after returning the bus to the storage yard.

Today's production was about an 18% increase in charge level on my Tesla Battery modules and the maximum production was 344 watts on the 375 watt panel.

In working on my automation's, definitely going to have to have a scenario for using excess solar production for when the bus is unoccupied.

freds
03-05-2020, 12:28 AM
Hey Freds, enjoyed reading your writeup of what you did. I almost went the Tesla S battery route as well. I didnt want to deal with a slightly non-standard voltage with that pack, as I think its using cells which sit at 3.7 instead of the more normal 3.2v x 4 cells that LiFePo4 cells work at. Glad you took it on, and hopefully it gives you good working margins. . .

I'm on my second lifepo4 install. This time using almost all Victron equipment as I love their bluetooth, victron connect, and vrm portal. Their inverters are awesome and I have a pair of them in split phase. Debating putting in an autotransformer to balance the inverters, but so far not too many problems with the split phase (outside of 30amp service).

The Victron controllers give you good manageabilty. They also now interface with some MFD devices in the marine world. So you can convert to NMEA2K and do some things on that front. The RV network and open marine one just hasnt taken off as much as NMEA2K still works.

Interesting choice on Pi. Its probably the cheapest and most flexible. Arduino might work better for battery bms type of work, but you have that covered. I had those same choices, but currently working off a PLC controller that does what I need to do. You may also want to look in to that, but it is a bit more costly than Pi, but the number of modules and things they have prebuilt is pretty extensive(proximity sensors, motion, etc). IFM makes some great mobile PLCs with CanNet network built in and all using CoDeSys development platforms. But again, pricy.

Anyhow, totally cool. Love to hear more as you progress. I'm also debating solar panels since there is so much real estate, but have to tackle a bunch of other projects up there.

Yes in using Tesla Battery modules they have different chemistry and are fully discharged at 19 volts, most inexpensive inverters where originally designed for lead acid battery's and turn off at 22 volts; which wastes a signification portion of the storage capacity.

I have been noodling away on how to handle 30 AMP 120 volt service and I would think just activate one inverter/charger to charge at the 120V level and have a manual switch to active that second.

I.E. If driveway surfing only draw 15 amps on 120, if plugged into 30 amp service enable an additional 15 amp draw.

Anthem
03-05-2020, 01:07 AM
Yes in using Tesla Battery modules they have different chemistry and are fully discharged at 19 volts, most inexpensive inverters where originally designed for lead acid battery's and turn off at 22 volts; which wastes a signification portion of the storage capacity.

I have been noodling away on how to handle 30 AMP 120 volt service and I would think just activate one inverter/charger to charge at the 120V level and have a manual switch to active that second.

I.E. If driveway surfing only draw 15 amps on 120, if plugged into 30 amp service enable an additional 15 amp draw.

If you are using Victron Inverters (I see some Victron equipment in there) - then if they are configured for split or parallel - it wont work if one of them is switched off. a quirk of them being combined. The issue is that you probably want the two to act as 1 - whether split or inverted so that you only deal with one CGGX/Cerbo/Venus GX device. .

But at that point - you might as well just plug in the 30amp and run it. If they are Victron, one will work, and the other will continue to invert. The one that is working, will charge whatever is being taken out from L2. People all jump up about this - but the reality is that you only have ONE 30amp leg anyhow. . Its not like you arent using the other leg - because you dont actually have another leg of power anyhow. . its shared one leg.

Your panel choice is excellent. the LG ones are the highest power ones out there right now. I would prefer to use the 60 cell intead of the 72 - but thats only because they are about 64in instead of 77 or something. The Sunpower X22 series is also excellent as they have better shading performance.

freds
03-08-2020, 04:55 PM
Just picked the bus up from the storage yard to work on it. Had one good day of sun and then it rained the rest of the week. House battery level is at 100%, started the week at 60%.