PDA

View Full Version : Nasty Inverter / Electrical Problem



Jon Wehrenberg
02-15-2010, 11:02 AM
On a Liberty 24V coach of my vintage there is a gauge on the dash that shows house voltage on the 24V side. For discussion purposes the normal displayed voltage with the bus connected to shore power, both inverters on and no serious loads, and fully charged batteries the voltage sits steady at 27Volts.

Yesterday I noticed the voltage needle was swinging from 27 up to being pegged at the top of the scale. For information purposes the inverters will shut down at 31 and come back on when the voltage drops.

To try to figure out what was happening I started by shutting the inverter charging circuits off one at a time. My initial thoughts were to isolate what I originally thought was a bad inverter. I had all the ceiling lights on while this was happening and they show a load of about 9 amps on the AC side so the charging circuits of the inverters were supplying charging current to satisfy the load.

Shutting each inverter off in turn did not stop the fluctuation of voltage. I think that rules out an inverter charger problem since both inverters alone were exhibiting the same voltage variations. I then shut off the lights using the master switch and after a while, although not immediately the voltage settled down to the normal range of 27V, but only with the #2 inverter on and #1 off. If I put #1 on, either in conjuction with #2 or alone both charging current in amps and voltage fluctuated up and down the scale.

With #2 on only, and no lighting loads the charging current sits at float and the voltage stays where it needs to be. But it only gets to a steady state after wild voltage swings for a while, which can vary from a few seconds to several minutes. I believe whatever the problem is relates more to the #1 inverter circuit, but since the two chargers are charging the same set of batteries (4 hooked in series and parallel like the chassis batteries) the problem is not with the inverter.

Since I can make either inverter fluctuate wildly I surmised the problem lies with what is common to the two inverters and not the inverters themselves. So I pulled the master DC panel out for inspection of all the master switches and the main curcuit breakers. I could not see any chafing, loose terminals, bad connections or anything to suggest a problem. The batteries are brand new and their connections are clean and tight.

I added insulation tape where there might be a possiblity of a short, I added some wire ties to the cable bundle (it did not do anything but make the cable bundle a tighter loom) and put things back together with the result being no change.

An inverter can exhibit the characteristics I described if the inverter supply AC power is somehow connected to the inverter 120V AC output which "bootstraps" the charger circuit with its own output power causing such voltage fluctuations on the 120VAC side. I will check that but that is almost impossible because of the fact each inverter supply is on a separate bus bar from the output and the outputs are on two separate bus bars.

The inverters are Freedom 2500 and have remote panels. The panels provide limited diagnostics, but nothing in terms of diagnostics that I cannot get with a multi-tester. I am getting voltage swings and I am getting charging currents that swing from high to low. What I don't know is where the inverters get their feedback that causes them to respond as they do. I know the battery cables from the inverters are the likely sources of the data the inverter chargers process, but what makes the feedback to the inverter drop so the charging voltage and current goes up is still a mystery. The swings are irregular and take place in a second or two. AC input power was 122-123 volts last night and is 121-122 this morning, so input voltage is steady and not an issue.


So what is the problem and where do I look?

MangoMike
02-15-2010, 11:52 AM
I have no solution.

But when Jon is looking for help we have a major "O CRAP MOMENT".

mike

dreamchasers
02-15-2010, 12:34 PM
Jon,

Since I just finished up with my inverter upgrade, perhaps I can offer some views. First, when the panel gauge is swinging, does the battery bus follow the swings (check with a volt meter at the DC bus source). If the battery voltage is stable, you could have a gauge issue. Secondly, if you battery bus is swinging as you described, a loose or dirty connection would be suspect. After replacing the battery lugs and cables on my Country Coach, I easily see that connection integrity is important on the heavy DC bus used by our coaches.

I would doubt that your battery buss is actually swinging (Serious!), but if it is, a bad connection or bad battery could be an issue. Also, if you suspect a battery, point a IR heat detector at each battery to look for temperature differences. If a bad battery is loading your DC bus that much, heat will be the by product.

Let us know what the outcome is.


Hector

Jon Wehrenberg
02-15-2010, 12:50 PM
All connections are clean and tight. I made sure of that when I replaced the batteries last fall, and verified it this morning.

Yes the voltages are swinging and no it is not a gauge issue. I have verified this with the multi-tester.

I spoke to Troy at Liberty (the Stuart service guru) and he suspects a triac failure in one or both inverters (I am not a believer in simultaneous failures) but until I can access my inverters (located beneath the bed and requiring substantial disassembly for access) I will not be able to verify this. Once I get to the inverters whether they need triacs or not they will be replaced and all cable connections at and in the vicinity of the inverters will be checked and tightened if necessary.

Forgot to mention I am letting the batteries discharge now with the inverter / chargers off. I will look for unusual discharge rates as well as elevated temps after re-charging.

sawdust_128
02-15-2010, 12:56 PM
Jon:

Do you see the same result while on shore power, generator and alternator? I have seen something similar to this and in checking my notes it turned out to be bad power comming into the coach from the shore source. But, you and I have explore the differences of the wiring system of my coach.

Have you verified the swing on the guage with actual voltages at the batteries? Is it possible that there is a loose connection/short in the instrumentation and not actually a voltage fluctuation?

Have you taken the inverters through a reset (if your inverters allow it)?

******************On edited *****************
After I posted this up, I saw the other comments.

Jon Wehrenberg
02-15-2010, 01:07 PM
The shore power is clean and steady at the voltages listed above. I reset the inverters by removing all power and then restarting them. The voltages at the battery terminals fluctuate as does the dash house voltage gauge and as does BOTH inverter voltage displays.

The alternator does not run through the inverters, but merely charges batteries, its voltage regualted by Mr. Delco Remy.

The alternator cable at some point (after going through the isolator) joins with the battery charger cables from the inverters. I have no diagram so I don't know which cable is which because once they disappear into the hidden recesses of the bus I lose track of them. There must be 15 or more, all are black, some vary from the common size but there are enough of the same size to make identifying one from another without a wire diagram unlikely. There are so many connections and cables I will not start disassembling stuff until I can have several days in a row to work on this issue, something I do not have now because we leave on a trip in one day.

truk4u
02-15-2010, 01:45 PM
Jon,

When your getting the fluctuations in house charging voltage, check the D/C amps at both inverters and see if there is a big hit of D/C being consumed.

On my dash I have the 24 volt gauge also, but since mine is a naked lady, my gauge is chassis only. But, When I have the chassis charger on even in the float mode, the 24 volt dash gauge get pegged beyond 30 volts! I checked the actual current at the batteries and they are getting the 13.2 float as they should. I only mention this because the gauge is wacky on the charger, but normal when running.

Wow, what a rare event, the Master asking for help!;)

mike kerley
02-15-2010, 04:02 PM
Jon, It sure sounds like a connection issue. Did you actually remove and clean the battery contacts or just check to see if they were tight? How about a bad crimp on a cable?

Has the bus been colder than normal as of late? Are the inverters always on and online, keeping warm? Perhaps an electrical connection internal to the inverters, with one ghosting the other. Are the Triac's heat sunk to the chassis? Cold causing contraction and poor contact.

Jon Wehrenberg
02-15-2010, 04:13 PM
Connection issues will be my focus. I verified all the connections at the batteries and the main panel located in the battery compartment. Two areas I have not yet accessed and will not until we have time and that is where the cables meet at a terminal block under the bed and at the chassis ground near the engine. Tomorrow I will do some of this checking.

When the batteries were replaced this fall all connections were wire wheel cleaned, all cables were unfastened from their terminals and wire wheel cleaned and new bolts were used if there had been any sign of corrosion.

Throughout today I have been looking for warm connections and any other indicators of loose or faulty connections, but except for the ones mentioned above I have seen no corroded or loose connections.

MICHAEL BELL
02-15-2010, 05:17 PM
Hey Jon, sounds like pending an investigative inspection of the inverters and connections there, you are on the right track. The thing about the inverters is that there are output filter circuits that can be damaged by severe ripple, which could have been caused by a failure in one inverter. By this I mean that both could have a problem, just not the [I]same problem[I] Please let me know what you find, or if you need further assistance. Wish I was near you to aid in your investigation. Sincerely, Ben 813-830-8619.

JIM KELLER
02-16-2010, 06:13 AM
Hey Ben, Nice to see you on the forum !

Jon Wehrenberg
02-16-2010, 08:13 AM
Thank's Ben.

For those new to POG, Ben is an electrical guru who is now associated with a relatively new company in the Tampa area that services Prevost conversions. Ben has participated in POG rallies providing service and seminars.

Ben, you guys need to get the word out and by getting a sponsorship here on the POG and Prevost stuff site you will announce to the world you are open for business. I'm sure Skiffer would welcome a new sponsor.

JIM CHALOUPKA
02-16-2010, 08:46 AM
Jon said,"On a Liberty 24V coach of my vintage there is a gauge on the dash that shows house voltage on the 24V side. For discussion purposes the normal displayed voltage with the bus connected to shore power, both inverters on and no serious loads, and fully charged batteries the voltage sits steady at 27Volts.

Yesterday I noticed the voltage needle was swinging from 27 up to being pegged at the top of the scale. For information purposes the inverters will shut down at 31 and come back on when the voltage drops."

Jon, is this condition of voltage pulsing the same with all combination s of engine running and engine off, with key on and not running.

What happens when the alternator is out of the picture?

Could this be a voltage regulator issue?





.

JIM CHALOUPKA
02-16-2010, 09:07 AM
Jon, are you referring to the gauge on the right in the picture?

Jon Wehrenberg
02-16-2010, 09:28 AM
I have not run the bus. This issue is solely related to the inverters and their output.

I have not run the generator. The inverters may or may not act up on generator power, but since the generator is not going to be run in my garage I have no way of knowing at this time. FWIW I doubt if this relates to input voltage which has remained steady.

It not only shows fluctuation on the dash gauge (house) but it shows on the LEDs on the remote panels. All have been verified by measuring with a multitester at the batteries and the equalizer.

Ironically, the problem went away last night. I will check more terminals and connections today.

JIM KELLER
02-16-2010, 09:42 AM
THE PROBLEM WENT AWAY ! That makes this a two person job. One wiggling wires and one watching a meter !

JIM CHALOUPKA
02-16-2010, 09:52 AM
Jon said, "On a Liberty 24V coach of my vintage there is a gauge on the dash that shows house voltage on the 24V side."

Jon, glad your problem went away!

Wondering where on your dash are you shown the voltage readings of which you speak?
Do I have such a gauge in the picture I posted?



:confused:

rfoster
02-16-2010, 10:25 AM
That's Great news Jon. The promise of warm air cures alot of stuff.

Jon Wehrenberg
02-16-2010, 11:38 AM
Jim C., you only have two dash gauges relating to electric, one labeled house to the right of the chassis volt/amp meter.

Jim Keller, You described what I have been doing. I have literally been tugging hard on all of the connections at the batteries and the switch / CB panel while watching my meter. Ditto when I played with the ground studs.

I tightened one of the ground cable connections by about a 5 degree turn on the wrench, the second one being so tight I will work on that when I check the remaining cable connections beneath the bed, those being worked on when I have the internals for my inverters so I can "rebuild" them as long as I am getting to them.

As of now I am thinking if I have a connection issue it is beneath the bed.

As of 10 minutes ago the voltages on both inverters were rock solid and have been all morning. This intermittent stuff is the kind of stuff that would drive a person to drink. Isn't it five O'clock somewhere?

JIM CHALOUPKA
02-16-2010, 12:17 PM
Jim C., you only have two dash gauges relating to electric, one labeled house to the right of the chassis volt/amp meter.


I know about those two Jon, I want to know where your gauge is located on the dash, the one you referenced in your first post.
Was it an option or did you add it?


:confused:

Jon Wehrenberg
02-16-2010, 12:39 PM
I have the same dash and gauges you do Jim.

With the exception of your Crestron screen on the left in lieu of the square lighted push buttons our dashes are the same.

hhoppe
02-16-2010, 09:49 PM
Jon: Ease up on the Viagra use and the terminal connections under the bed won't loosen up as often.

michaeldterry
02-17-2010, 08:08 AM
Jon: Ease up on the Viagra use and the terminal connections under the bed won't loosen up as often.

Shots fired! :eek:

truk4u
02-17-2010, 09:13 AM
Harry,

It's the Lawrence Welk music that gets him fired up, Viagra puts him to sleep!:D

merle&louise
08-15-2010, 10:14 PM
I am having some inverter problems. Does anyone have the name of the guy in New Mexico or Arizona that fixes inverters. Mine is a Freedom 2500, and it is not inverting. I tried to reset it; disconnect and wait 30 minutes for it to reset, but it still won't invert. The battery charger works fine, but the unit just won't invert.

I would like to send it off to be repaired, but I can't find this guy's name and address.

gmcbuffalo
08-16-2010, 12:26 AM
Tuga I just went thru this myself, I found that there was a Circuit Breaker button and I just pushed it and it started working. It didn't look tripped, I just pushed it becuase I couldn't explain why it wasn't working.
GregM

ajducote
08-16-2010, 07:35 AM
I am having some inverter problems. Does anyone have the name of the guy in New Mexico or Arizona that fixes inverters. Mine is a Freedom 2500, and it is not inverting. I tried to reset it; disconnect and wait 30 minutes for it to reset, but it still won't invert. The battery charger works fine, but the unit just won't invert.

I would like to send it off to be repaired, but I can't find this guy's name and address.

Tuga,

I found this thread. I believe this is what you are looking for.

http://forum.prevostownersgroup.com/showthread.php?3311-Inverter-Repair&highlight=inverter

merle&louise
08-16-2010, 08:43 AM
Greg,

I checked the 3 30 amp breakers on the front of the inverter; they were not tripped.

Do you have a Freedom 2500 inverter? If so, where is the breaker you reset located?

Thanks for your post.

Andre,

Thanks, that's the name I was looking for; I will add it to my information page.

Woody
08-16-2010, 11:31 AM
Tuga

My 2500 has a breaker on the upper left hand side about half way back. I can't see it because of how the unit is mounted but I have had to reset it by feel.

gmcbuffalo
08-16-2010, 12:00 PM
Tuga my current coach has 458's

merle&louise
08-16-2010, 06:07 PM
Thanks Greg and Woody. I will look for the c.b. or reset button in the morning.