flyu2there
11-29-2009, 08:16 AM
While preparing my top for a coat of tape coat, I removed the three covers for the roof air units. Mine were attached to the units by four sheet metal screws, two on the rear sides and two on the front of each housing.
Here is what I found. Of the twelve drilled holes in the covers, 9 of them showed stress cracks and three of them failed (broke apart) when I removed the screws, obviously the work of over torque and sun/heat. Whoever last worked on them (I admit, it wasn't me) put in larger pan heads screws as the fix for something that is obviously a weak link....the effect only delays the inevitable. For years I have seen these covers laying on the side of a number of highways throughout the land and my time was close by what I found. My fix was to re enforce all of the mounting holes with fiberglass and then to re drill the screw holes, followed by prep and paint.
Issue number two.......... Inside of these units you will find foam rubber strips which apparently serve as ducting for the condensor. All of my foam rubber was decayed and needed to be replaced (available at Loews).
A little contact cement did the job and the pattern is clearly visible inside of the covers.
Issue number three.......... The package unit itself was filthy inside and the condensor, although mine were all very operational, was at least partially plugged with dirt and debris. Compressed air and a couple of cans of coil cleaner did the job. I suspect that I had some loss of efficiency with all of the filth.
Admittedly these thing are a royal pain to get at, however I now believe that an annual inspection is a requirement. I will post some pictures soon on this one.
Here is what I found. Of the twelve drilled holes in the covers, 9 of them showed stress cracks and three of them failed (broke apart) when I removed the screws, obviously the work of over torque and sun/heat. Whoever last worked on them (I admit, it wasn't me) put in larger pan heads screws as the fix for something that is obviously a weak link....the effect only delays the inevitable. For years I have seen these covers laying on the side of a number of highways throughout the land and my time was close by what I found. My fix was to re enforce all of the mounting holes with fiberglass and then to re drill the screw holes, followed by prep and paint.
Issue number two.......... Inside of these units you will find foam rubber strips which apparently serve as ducting for the condensor. All of my foam rubber was decayed and needed to be replaced (available at Loews).
A little contact cement did the job and the pattern is clearly visible inside of the covers.
Issue number three.......... The package unit itself was filthy inside and the condensor, although mine were all very operational, was at least partially plugged with dirt and debris. Compressed air and a couple of cans of coil cleaner did the job. I suspect that I had some loss of efficiency with all of the filth.
Admittedly these thing are a royal pain to get at, however I now believe that an annual inspection is a requirement. I will post some pictures soon on this one.